Swapped out the 150A breaker for one with M8 studs. Doing some research and now surprised that so many high current breakers come with M6 studs. Nowhere near big enough to be able to handle 100A plus.
Also discovering a lot about how these DC breakers work and the actual point at which they will trip. This is from ambient temp of 25C
Current (Amperes) | Overload Multiplier | Estimated Time to Trip
• 150.0A | 1.00x | Indefinite (Will not trip)
• 165.0A | 1.10x | 30 minutes to 2 hours
• 187.5A | 1.25x | 5 minutes to 15 minutes
• 202.5A | 1.35x | 2 minutes to 8 minutes
• 300.0A | 2.00x | 15 seconds to 45 seconds
• 750.0A | 5.00x | 2 seconds to 10 seconds
• 1500.0A | 10.0x | < 0.1 seconds (Magnetic Trip)
But something else has come up. If i were to run at 2Kw, the current draw on the battery would be around 190A. However, the continuous discharge current of the battery, as controlled by the BMS, is 200A. As the voltage of the battery drops during discharge, the current will rise. So if I ran it flat out (which I don't intend to do) then the BMS may shut the battery down...
It's never ending....
Home Solar System
Re: Home Solar System
A major advance in our solar adventure.
The Ecoflow Stream Microinverter arrived which prompted me to nudge MrJJ to install the solar panels, which he did today.
I just have to show off his handiwork
See pics below.
The mountings comprise 4 x angular frames made from treated and painted timber.
Pitched at 20% as a compromise between solar efficiency and wind resistance, These panels are HUGE 2.4m x 1.2m and 605W each!!!! They weigh about 33kilos apiece.
For ballast, we currently have about 100kg of concrete bricks and there is a ballast tray on which I intend to load four bale arm trays full of bottled water. Might as well use the storage space.
We still need to install the inverter inside the garage, once we have procured 4 x 5m PV extension cables ( Or I could mount the inverter under the panels )
*Evil ecoflow sneakily didn't include PV cables, having changed what's in the bundle.
The Ecoflow Stream Microinverter arrived which prompted me to nudge MrJJ to install the solar panels, which he did today.
I just have to show off his handiwork
The mountings comprise 4 x angular frames made from treated and painted timber.
Pitched at 20% as a compromise between solar efficiency and wind resistance, These panels are HUGE 2.4m x 1.2m and 605W each!!!! They weigh about 33kilos apiece.
For ballast, we currently have about 100kg of concrete bricks and there is a ballast tray on which I intend to load four bale arm trays full of bottled water. Might as well use the storage space.
We still need to install the inverter inside the garage, once we have procured 4 x 5m PV extension cables ( Or I could mount the inverter under the panels )
*Evil ecoflow sneakily didn't include PV cables, having changed what's in the bundle.
Graceful Degradation! Prepping's objective summed up in two words. Turning Disaster into Mild Inconvenience by the power of fore-thought
Not Feeling Optimistic. Let me be wrong
Not Feeling Optimistic. Let me be wrong
-
Yorkshire Andy
- Posts: 9866
- Joined: Thu Oct 03, 2013 4:06 pm
Re: Home Solar System
Should see the negative feedback piling in on eBay
If your roughing it, Your doing it wrong 
Lack of planning on your part doesn't make it an emergency on mine
Lack of planning on your part doesn't make it an emergency on mine
Re: Home Solar System
Impressive. It looks like Mr JJ did a lot of hard work to build all that. Must have taken awhile.jennyjj01 wrote: ↑Sun May 03, 2026 7:28 pm A major advance in our solar adventure.
The Ecoflow Stream Microinverter arrived which prompted me to nudge MrJJ to install the solar panels, which he did today.
I just have to show off his handiworkSee pics below.
The mountings comprise 4 x angular frames made from treated and painted timber.
Pitched at 20% as a compromise between solar efficiency and wind resistance, These panels are HUGE 2.4m x 1.2m and 605W each!!!! They weigh about 33kilos apiece.
For ballast, we currently have about 100kg of concrete bricks and there is a ballast tray on which I intend to load four bale arm trays full of bottled water. Might as well use the storage space.
We still need to install the inverter inside the garage, once we have procured 4 x 5m PV extension cables ( Or I could mount the inverter under the panels )
*Evil ecoflow sneakily didn't include PV cables, having changed what's in the bundle.
solar1.jpgsolar2.jpg
Is the house on the left in the pics, so it will block wind coming from that side getting under the panels? I assume they are fixed to the timber.
I wouldn't have the space. My garden is long, but even narrower than the house, which is terraced, and the hedge takes up a chunk, and would block the sun to a large extent as well. The fence on the left does face south though, as does one wall of the kitchen and back bedroom. Back of house faces NWN so only gets sun in the morning.
Re: Home Solar System
Thanks. He was pretty quick with his power tools. Blame me for the design where I had to relearn all about triangles
Next door is on the left and mine is on the right, but offset, forward. It stops wind coming direct into the 'sail' of the panels. They are not screwed down and we are trusting several hundred kilo of ballast to hold them. More to be added.Is the house on the left in the pics, so it will block wind coming from that side getting under the panels? I assume they are fixed to the timber.
[/quote]
I wouldn't have the space. My garden is long, but even narrower than the house, which is terraced, and the hedge takes up a chunk, and would block the sun to a large extent as well. The fence on the left does face south though, as does one wall of the kitchen and back bedroom. Back of house faces NWN so only gets sun in the morning.
[/quote]
Mine will get max sun between about 10am and 1pm then will start to get shaded by my house until about 3pm. Before and after that, they will be at a bad angle looking 90ø away from the sun. Far from ideal. I might try facing them West so they max out in the early evening, but that will mean they get very little before 3pm.
I would like a proper ac linked solar battery, but they would never cost in , not in a lifetime.
Total cost so far £349 and I need to spend £40 on cables. Estimated payback time 4-5 years at current rates.
.
Graceful Degradation! Prepping's objective summed up in two words. Turning Disaster into Mild Inconvenience by the power of fore-thought
Not Feeling Optimistic. Let me be wrong
Not Feeling Optimistic. Let me be wrong
Re: Home Solar System
Oh, is this on a garage roof?
-
GeraldTheBonzai
- Posts: 347
- Joined: Fri Oct 08, 2021 7:52 pm
Re: Home Solar System
So thats 4*605W? 2.4Kw? How are you going to wired them into the micro inverter, as I though they only has 2 MPPT channels? Or is that 2 panels? Hard to tell.